Welcome to the JREF Forum, where we discuss skepticism, critical thinking, the paranormal and science in a friendly but lively way. You are currently viewing the forum as a guest, which means you are missing out on discussing matters that are of interest to you. Please consider registering so you can gain full use of the forum features and interact with other Members. Registration is simple, fast and free! Click here to register today.

Tags ups , wtc2

Reply
Old 8th February 2010, 10:02 PM   #1
pgimeno
Critical Thinker
 
pgimeno's Avatar
 
Join Date: Feb 2009
Location: Spain
Posts: 335
Importance of UPS in South Tower

I've seen some recent discussion relative to the catenary forces that pulled the perimeter columns in WTC 2. I was wondering if this has been taking into account:

http://undicisettembre.blogspot.com/...r-of-wtc2.html

I think NIST didn't consider that factor directly, as the references to the UPS system reduced merely to stating that it existed and caused the tenants to reinforce the floors.

Could that extra weight have a significant role in the pulling of the perimeter columns?
pgimeno is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 8th February 2010, 10:08 PM   #2
BCR
Graduate Poster
 
BCR's Avatar
 
Join Date: Dec 2008
Location: Memphis
Posts: 1,206
So are you saying that UPS delivered the package the bomb in it?
BCR is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 9th February 2010, 12:22 AM   #3
PB2007
This line left intentionally blank
 
PB2007's Avatar
 
Join Date: Jul 2007
Location: Here and now
Posts: 234
deleted
PB2007 is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 9th February 2010, 01:20 AM   #4
Dave Rogers
The Unbanned
 
Dave Rogers's Avatar
 
Join Date: Jan 2007
Location: Notlob
Posts: 10,093
Originally Posted by pgimeno View Post
I think NIST didn't consider that factor directly, as the references to the UPS system reduced merely to stating that it existed and caused the tenants to reinforce the floors.
It appears from Henry's website that NIST didn't consider it directly because they didn't have any documentation of the strengthening applied or the loads present.

Originally Posted by pgimeno View Post
Could that extra weight have a significant role in the pulling of the perimeter columns?
Could have, but it appears that the extra weight was applied mostly in the two-way trussed corner section, where any catenary action would have primarily caused a lateral deflection of the one-way trusses. I would expect it to have less effect on the perimeter columns than additional weight near the mid-point of a floor side.

Dave
__________________
"I guess for Truthers the great thing about Google is that it abolishes context automatically, thus saving your precious reserves of stupid for more important tasks." - Dr. Adequate

GENERATION 6: The first time you see this, copy it into your sig on any forum and add 1 to the generation. Social experiment.
Dave Rogers is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 10th February 2010, 09:45 AM   #5
jaydeehess
Philosopher
 
jaydeehess's Avatar
 
Join Date: Nov 2006
Location: 40 miles from the border
Posts: 5,459
Originally Posted by Dave Rogers View Post
It appears from Henry's website that NIST didn't consider it directly because they didn't have any documentation of the strengthening applied or the loads present.



Could have, but it appears that the extra weight was applied mostly in the two-way trussed corner section, where any catenary action would have primarily caused a lateral deflection of the one-way trusses. I would expect it to have less effect on the perimeter columns than additional weight near the mid-point of a floor side.

Dave
Interesting read.
The TV company I work for has two medium sized UPS units. One is 750VA the other 1500 VA. The former, with the additional optional battery pack weighs 600 pounds. The other is approx double that. These can keep our TV station and the cable TV head end (including a dozen computer servers) running for about one hour.
The weight of these units is the equivalent of nine 200 pound men but they do not utilise the battery type shown in the article. They use 12V batteries that resemble the ones found in automobiles.

On the other hand I used to work for Transport Canada and we replaced the old RUPU (Rotary Uninterruptible Power Supply), which was a large electric motor that turned a heavy flywheel and an AC generator. the AC generator supplied the radar equipment. The flywheel would keep the generator turning, in the event of a power failure, long enough for the diesel to start up and supply current to the electric motor (almost perfect isolation from line spikes and surges). This RUPU was replaced with a battery bank of the type shown in the article. IIRC 72 batteries were needed to run the radar long enough for a diesel genset to kick in. There was another bank of 24 of this type that supplied back up for the radio equipment.
__________________
"Math, science, history, unraveling the mystery, that all started with a Big Bang,,,Bang!

No aircraft hit the Pentagon and the damage was caused by something else. Yes, CiT=no planers
jaydeehess is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 10th February 2010, 09:58 AM   #6
MG1962
Philosopher
 
MG1962's Avatar
 
Join Date: Sep 2006
Posts: 5,586
Even if the reinforcing of the flooring played no part in the collapse. At least we have a good alternate answer to that material flow. The NIST always said their answer was an educated guess.

Great peice of research
MG1962 is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 10th February 2010, 11:56 AM   #7
BigAl
Illuminator
 
BigAl's Avatar
 
Join Date: Jun 2007
Posts: 4,641
Originally Posted by jaydeehess View Post
Interesting read.
The TV company I work for has two medium sized UPS units. One is 750VA the other 1500 VA. The former, with the additional optional battery pack weighs 600 pounds. The other is approx double that. These can keep our TV station and the cable TV head end (including a dozen computer servers) running for about one hour.
The weight of these units is the equivalent of nine 200 pound men but they do not utilise the battery type shown in the article. They use 12V batteries that resemble the ones found in automobiles.
I ran a data center with a 60kva load, the UPS was good for 20 minutes. The battery room looked like something out of a diesel-electric submarine. I couldn't imagine how many tons of lead we had in there.

It would be easy to imagine a comparable data center and UPS in the Fuji Bank facility (is that what it was?) on 9/11.
__________________
------
Eric Pode of Croydon
Chief Assistant to the Assistance Chief,
Dept of Redundancy Dept.
BigAl is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 10th February 2010, 12:28 PM   #8
Sam.I.Am
Graduate Poster
 
Sam.I.Am's Avatar
 
Join Date: Apr 2009
Location: Taking a "Hollywood" in the rain locker
Posts: 1,254
Originally Posted by BigAl View Post
I ran a data center with a 60kva load, the UPS was good for 20 minutes. The battery room looked like something out of a diesel-electric submarine. I couldn't imagine how many tons of lead we had in there.
Unless there were 126 4' tall, 18" square battery cells crammed into a space so tight that you had to crawl on top of the batteries to get around then it probably looked nothing like a submarines battery well.
__________________
"Swift, silent and deadly" was a part of my job description Upon hearing me say that my friend asked me "So you're a fart?"...

About my avatar.
Sam.I.Am is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 10th February 2010, 12:31 PM   #9
pgimeno
Critical Thinker
 
pgimeno's Avatar
 
Join Date: Feb 2009
Location: Spain
Posts: 335
Originally Posted by Dave Rogers View Post
It appears from Henry's website that NIST didn't consider it directly because they didn't have any documentation of the strengthening applied or the loads present.
Sad how sometimes some important factors that we can't see or don't have data about them turn out to be crucial to understand an event. I'm not saying it's the case here though.

Originally Posted by Dave Rogers View Post
Could have, but it appears that the extra weight was applied mostly in the two-way trussed corner section, where any catenary action would have primarily caused a lateral deflection of the one-way trusses. I would expect it to have less effect on the perimeter columns than additional weight near the mid-point of a floor side.
I see. I suppose that some lateral deflection would be expectable in that case, which was not observed AFAIK. So it seems we can in principle rule out a significant role of that extra weight in the collapse.
pgimeno is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 10th February 2010, 12:53 PM   #10
BigAl
Illuminator
 
BigAl's Avatar
 
Join Date: Jun 2007
Posts: 4,641
Originally Posted by Sam.I.Am View Post
Unless there were 126 4' tall, 18" square battery cells crammed into a space so tight that you had to crawl on top of the batteries to get around then it probably looked nothing like a submarines battery well.
Was this on a nuke? I assume a nuke needs backup power.
__________________
------
Eric Pode of Croydon
Chief Assistant to the Assistance Chief,
Dept of Redundancy Dept.
BigAl is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 10th February 2010, 01:11 PM   #11
Sam.I.Am
Graduate Poster
 
Sam.I.Am's Avatar
 
Join Date: Apr 2009
Location: Taking a "Hollywood" in the rain locker
Posts: 1,254
Originally Posted by BigAl View Post
Was this on a nuke? I assume a nuke needs backup power.
Yes. All nuke boats have a diesel generator (DC) and batteries as well as the nuclear power plant. They also have 2 other modes of propulsion using DC (one is independent of the main shaft) so that we could always limp back into port if something happened either to the reactor or the main shaft.

The batteries are your final power source and the technology is proven through decades of use on hundreds of boats since before WWII. They have improved the cells somewhat since then but that had more to do with changing the plating than anything else. The size and configuration is the same.
__________________
"Swift, silent and deadly" was a part of my job description Upon hearing me say that my friend asked me "So you're a fart?"...

About my avatar.
Sam.I.Am is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Old 11th February 2010, 01:18 AM   #12
Dave Rogers
The Unbanned
 
Dave Rogers's Avatar
 
Join Date: Jan 2007
Location: Notlob
Posts: 10,093
Originally Posted by pgimeno View Post
I see. I suppose that some lateral deflection would be expectable in that case, which was not observed AFAIK. So it seems we can in principle rule out a significant role of that extra weight in the collapse.
I doubt we can be certain either way, really. Any lateral deflection of the one-way bridging trusses would be inside the building, and hence unobservable from outside. It would cause some pull-in, from simple geometry, but I think it would be impossible to separate which bit of weight caused how much of the total pull-in.

Dave
__________________
"I guess for Truthers the great thing about Google is that it abolishes context automatically, thus saving your precious reserves of stupid for more important tasks." - Dr. Adequate

GENERATION 6: The first time you see this, copy it into your sig on any forum and add 1 to the generation. Social experiment.
Dave Rogers is offline   Quote this post in a PM   Nominate this post for this month's language award Copy a direct link to this post Reply With Quote Back to Top
Reply

JREF Forum » General Topics » Conspiracy Theories » 9/11 Conspiracy Theories

Bookmarks

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On